Electrical light post question

Post by Toecutter1978 » Sun Nov 01, 2020 12:22 pm

I have an outside post light that I have been wanting to replace the fixture as it has not worked since moving in. So I finally found one I liked and installed it. Well the new one does not receive any power. The switch is good, and there is power to the junction box going outside to the wires that go into the ground.

So from that junction box to the post is the wiring that is in the ground, which leads me to think there either has to be a break in it or something. Now that wire does not look like it is ran in any conduit in the ground, more likely it was just placed in a shallow trench and called it a day.

My question is how deep should I bury a new wire and what do I put it in? Is the correct depth 18”?
IMG_0063.jpg
IMG_0063.jpg

Sent from my iPhone using Tapatalk
Attachments
IMG_0062.jpg

User avatar
Gunsmokin
KAC Member
KAC Member
Posts: 5076
Joined: Wed Jul 25, 2012 9:11 pm
Location: Louisville
Has liked: 1 time
Been liked: 20 times

Re: Electrical light post question

Post by Gunsmokin » Sun Nov 01, 2020 1:20 pm

Looks like the wire that is existing isn’t underground wire. Looks like regular romex. That could be part of your problem. Could be corroded/shorted out. Underground/direct bury rated wire doesn’t have paper in it like regular romex. If you’re going to dig a trench, you may as well lay some conduit in there for the wire. Still use underground wire. I just wouldn’t bury it directly in the ground out in an open area where someone could dig a hole and hit it.


Sent from my iPhone using Tapatalk
jackalo626 wrote:Skibble dee dibbledy

User avatar
Gunsmokin
KAC Member
KAC Member
Posts: 5076
Joined: Wed Jul 25, 2012 9:11 pm
Location: Louisville
Has liked: 1 time
Been liked: 20 times

Electrical light post question

Post by Gunsmokin » Sun Nov 01, 2020 1:21 pm

I would dig it at least 18” deep. Just my $.02


Sent from my iPhone using Tapatalk
jackalo626 wrote:Skibble dee dibbledy

User avatar
plumber_bob
KAC Member
KAC Member
Posts: 6774
Joined: Sun Feb 02, 2014 2:25 pm
Location: L.J. Ky
Has liked: 174 times
Been liked: 80 times

Re: Electrical light post question

Post by plumber_bob » Sun Nov 01, 2020 3:34 pm

What Tim said.

pb
"One Man With Courage is a Majority"

User avatar
rustynuts
KAC Member
KAC Member
Posts: 14171
Joined: Sun Feb 10, 2013 8:29 pm
Location: Bardstown
Has liked: 47 times
Been liked: 80 times

Re: Electrical light post question

Post by rustynuts » Sun Nov 01, 2020 5:24 pm

What not-Bob and Tim said.

User avatar
Niceguy
KAC Member
KAC Member
Posts: 14202
Joined: Thu Apr 05, 2012 2:57 pm
Location: Smithfield Ky
Has liked: 327 times
Been liked: 92 times

Re: Electrical light post question

Post by Niceguy » Sun Nov 01, 2020 7:07 pm

Borrow Iron83848558483's pole digger truck and bury that bitch about 10 feet deep and throw an extension cord out to it...

Sent from my SM-N981U using Tapatalk


User avatar
Niceguy
KAC Member
KAC Member
Posts: 14202
Joined: Thu Apr 05, 2012 2:57 pm
Location: Smithfield Ky
Has liked: 327 times
Been liked: 92 times

Re: Electrical light post question

Post by Niceguy » Sun Nov 01, 2020 7:08 pm

And put about 10-20' yards of concrete in the hole because you don't want that sucker to blow over either...

Sent from my SM-N981U using Tapatalk


User avatar
Niceguy
KAC Member
KAC Member
Posts: 14202
Joined: Thu Apr 05, 2012 2:57 pm
Location: Smithfield Ky
Has liked: 327 times
Been liked: 92 times

Re: Electrical light post question

Post by Niceguy » Sun Nov 01, 2020 7:09 pm

I'm not a professional though...

Sent from my SM-N981U using Tapatalk


User avatar
Gunsmokin
KAC Member
KAC Member
Posts: 5076
Joined: Wed Jul 25, 2012 9:11 pm
Location: Louisville
Has liked: 1 time
Been liked: 20 times

Re: Electrical light post question

Post by Gunsmokin » Sun Nov 01, 2020 7:51 pm

plumber_bob wrote:What Tim said.

pb
Image


Sent from my iPhone using Tapatalk
jackalo626 wrote:Skibble dee dibbledy

Rem700
KAC Member
KAC Member
Posts: 13301
Joined: Sun Mar 04, 2012 9:47 am
Location: Definitely at my soul crushing job!
Has liked: 110 times
Been liked: 56 times

Re: Electrical light post question

Post by Rem700 » Mon Nov 02, 2020 7:09 am

Agreed with above. If your digging already, use conduit and underground wire. Go 18-24 inches down

User avatar
iron369
KAC Member
KAC Member
Posts: 4870
Joined: Mon Feb 17, 2014 11:43 am
Location: Valley Station
Has liked: 71 times
Been liked: 96 times

Re: Electrical light post question

Post by iron369 » Mon Nov 02, 2020 8:33 am

While the auger truck is the more fun suggestion, it’s also a little overkill.
What you have is probably direct burial cable. It looks a lot like romex, but it’s made to be directly buried in the ground without a raceway. Conduit is always a better option if properly installed. The chart I’m posting should help you out with whatever direction you want to go when installing the new wiring. Image
Using Tapatalk

User avatar
Toecutter1978
KAC Member
KAC Member
Posts: 10474
Joined: Sun Oct 27, 2013 8:08 pm
Location: Brooks
Has liked: 0
Been liked: 14 times

Re: Electrical light post question

Post by Toecutter1978 » Mon Nov 02, 2020 8:42 am

Ok thank you! Is there a specific conduit you would suggest? Also should it be ran in a direct line or should I put a 90 degree turn in it?

I think I should call the dog people out also correct before I start so they can come mark stuff just in case, I don’t want to accidentally hit a gas line or something, but they should be deeper than 18” right?

User avatar
Toecutter1978
KAC Member
KAC Member
Posts: 10474
Joined: Sun Oct 27, 2013 8:08 pm
Location: Brooks
Has liked: 0
Been liked: 14 times

Re: Electrical light post question

Post by Toecutter1978 » Mon Nov 02, 2020 8:46 am

That circuit is NOT GFCI protected. That breaker controls a few light switches and electrical plugs. I guess the easiest way to make it would be to replace the breaker with one of those newer gfci ones huh.


Sent from my iPhone using Tapatalk

User avatar
Toecutter1978
KAC Member
KAC Member
Posts: 10474
Joined: Sun Oct 27, 2013 8:08 pm
Location: Brooks
Has liked: 0
Been liked: 14 times

Re: Electrical light post question

Post by Toecutter1978 » Mon Nov 02, 2020 8:47 am

Niceguy wrote:Borrow Iron83848558483's pole digger truck and bury that bitch about 10 feet deep and throw an extension cord out to it...

Sent from my SM-N981U using Tapatalk
That would be so awesome!! I wonder how far I could dig with that.


Sent from my iPhone using Tapatalk

User avatar
iron369
KAC Member
KAC Member
Posts: 4870
Joined: Mon Feb 17, 2014 11:43 am
Location: Valley Station
Has liked: 71 times
Been liked: 96 times

Re: Electrical light post question

Post by iron369 » Mon Nov 02, 2020 8:57 am

I’d put in schedule 40 pvc. Make sure the wire is rated for wet locations,ex. THWN and not THHN. Take it in as direct a path as possible. More bends make it harder to pull wire and there can’t be more than 360 degrees for bend in the run total.
Definitely get a BUD check. If you’re hand digging, it won’t make too much of a difference since you can just dig around anything already in the ground. It’s still better to know what’s there. You can ask them to not paint any concrete surfaces. Otherwise you will have green, yellow, blue, and red paint marks on your driveway for years.
These users liked the author iron369 for the post:
Rem700
Rating: 12.5%
Using Tapatalk

User avatar
iron369
KAC Member
KAC Member
Posts: 4870
Joined: Mon Feb 17, 2014 11:43 am
Location: Valley Station
Has liked: 71 times
Been liked: 96 times

Re: Electrical light post question

Post by iron369 » Mon Nov 02, 2020 8:58 am

Toecutter1978 wrote:
Niceguy wrote:Borrow Iron83848558483's pole digger truck and bury that bitch about 10 feet deep and throw an extension cord out to it...

Sent from my SM-N981U using Tapatalk
That would be so awesome!! I wonder how far I could dig with that.


Sent from my iPhone using Tapatalk
We dig pole bases 36” across and 16’ deep.
Using Tapatalk

User avatar
Niceguy
KAC Member
KAC Member
Posts: 14202
Joined: Thu Apr 05, 2012 2:57 pm
Location: Smithfield Ky
Has liked: 327 times
Been liked: 92 times

Re: Electrical light post question

Post by Niceguy » Mon Nov 02, 2020 9:03 am

iron369 wrote:
Toecutter1978 wrote:
Niceguy wrote:Borrow Iron83848558483's pole digger truck and bury that bitch about 10 feet deep and throw an extension cord out to it...

Sent from my SM-N981U using Tapatalk
That would be so awesome!! I wonder how far I could dig with that.


Sent from my iPhone using Tapatalk
We dig pole bases 36” across and 16’ deep.
My advice may or may not have influenced by alcohol...haha
I do think it's funny though. 36" x 16'?! That's what I'm talking about! Get on it Eric! haha

Sent from my SM-N981U using Tapatalk


User avatar
iron369
KAC Member
KAC Member
Posts: 4870
Joined: Mon Feb 17, 2014 11:43 am
Location: Valley Station
Has liked: 71 times
Been liked: 96 times

Re: Electrical light post question

Post by iron369 » Mon Nov 02, 2020 9:04 am

Toecutter1978 wrote:That circuit is NOT GFCI protected. That breaker controls a few light switches and electrical plugs. I guess the easiest way to make it would be to replace the breaker with one of those newer gfci ones huh.


Sent from my iPhone using Tapatalk
It definitely needs to be gfci.
Using Tapatalk

User avatar
Toecutter1978
KAC Member
KAC Member
Posts: 10474
Joined: Sun Oct 27, 2013 8:08 pm
Location: Brooks
Has liked: 0
Been liked: 14 times

Re: Electrical light post question

Post by Toecutter1978 » Mon Nov 02, 2020 9:24 am

Those gfci breakers are way larger than the standard breakers, I wonder if it will even fit in my panel.


Sent from my iPhone using Tapatalk

Rem700
KAC Member
KAC Member
Posts: 13301
Joined: Sun Mar 04, 2012 9:47 am
Location: Definitely at my soul crushing job!
Has liked: 110 times
Been liked: 56 times

Re: Electrical light post question

Post by Rem700 » Mon Nov 02, 2020 10:42 am

Toecutter1978 wrote:
Mon Nov 02, 2020 8:42 am
Ok thank you! Is there a specific conduit you would suggest? Also should it be ran in a direct line or should I put a 90 degree turn in it?

I think I should call the dog people out also correct before I start so they can come mark stuff just in case, I don’t want to accidentally hit a gas line or something, but they should be deeper than 18” right?
The easiest way is to rip that stupid light post out and cap the wire inside that LB on the house lol.....thats what i just did for mine cause i was tired of mowing around it!

Rem700
KAC Member
KAC Member
Posts: 13301
Joined: Sun Mar 04, 2012 9:47 am
Location: Definitely at my soul crushing job!
Has liked: 110 times
Been liked: 56 times

Re: Electrical light post question

Post by Rem700 » Mon Nov 02, 2020 10:44 am

Niceguy wrote:
Mon Nov 02, 2020 9:03 am
iron369 wrote:
Toecutter1978 wrote:
Niceguy wrote:Borrow Iron83848558483's pole digger truck and bury that bitch about 10 feet deep and throw an extension cord out to it...

Sent from my SM-N981U using Tapatalk
That would be so awesome!! I wonder how far I could dig with that.


Sent from my iPhone using Tapatalk
We dig pole bases 36” across and 16’ deep.
My advice may or may not have influenced by alcohol...haha
I do think it's funny though. 36" x 16'?! That's what I'm talking about! Get on it Eric! haha

Sent from my SM-N981U using Tapatalk
Thats good to know.....for getting rid of "problems" that require digging holes......

Rem700
KAC Member
KAC Member
Posts: 13301
Joined: Sun Mar 04, 2012 9:47 am
Location: Definitely at my soul crushing job!
Has liked: 110 times
Been liked: 56 times

Re: Electrical light post question

Post by Rem700 » Mon Nov 02, 2020 10:45 am

Toecutter1978 wrote:
Mon Nov 02, 2020 9:24 am
Those gfci breakers are way larger than the standard breakers, I wonder if it will even fit in my panel.


Sent from my iPhone using Tapatalk
They make some GFCI breakers that fit in a single pole breaker location.... or at least they did.

User avatar
Toecutter1978
KAC Member
KAC Member
Posts: 10474
Joined: Sun Oct 27, 2013 8:08 pm
Location: Brooks
Has liked: 0
Been liked: 14 times

Re: Electrical light post question

Post by Toecutter1978 » Mon Nov 02, 2020 11:11 am

Rem700 wrote:
Toecutter1978 wrote:
Mon Nov 02, 2020 9:24 am
Those gfci breakers are way larger than the standard breakers, I wonder if it will even fit in my panel.


Sent from my iPhone using Tapatalk
They make some GFCI breakers that fit in a single pole breaker location.... or at least they did.
Oh ok. Maybe the video I watched on how to replace one had to do with it being that it was one of those arc disruption breakers too.

That breaker was twice the size and from looking at my panel I do not know if it would fit behind it or not. I could see it not knowing my luck. I had to buy those slimmer gfci plugs that cost more because the plug boxes in the house are not the regular size or something.

Whom ever wired this place must have been I don’t know. Not an electrician.


Sent from my iPhone using Tapatalk

User avatar
iron369
KAC Member
KAC Member
Posts: 4870
Joined: Mon Feb 17, 2014 11:43 am
Location: Valley Station
Has liked: 71 times
Been liked: 96 times

Re: Electrical light post question

Post by iron369 » Mon Nov 02, 2020 3:56 pm

Toecutter1978 wrote:
Rem700 wrote:
Toecutter1978 wrote:
Mon Nov 02, 2020 9:24 am
Those gfci breakers are way larger than the standard breakers, I wonder if it will even fit in my panel.


Sent from my iPhone using Tapatalk
They make some GFCI breakers that fit in a single pole breaker location.... or at least they did.
Oh ok. Maybe the video I watched on how to replace one had to do with it being that it was one of those arc disruption breakers too.

That breaker was twice the size and from looking at my panel I do not know if it would fit behind it or not. I could see it not knowing my luck. I had to buy those slimmer gfci plugs that cost more because the plug boxes in the house are not the regular size or something.

Whom ever wired this place must have been I don’t know. Not an electrician.


Sent from my iPhone using Tapatalk
If you have a picture of your panel or some information about it, I may be able to direct you to the breaker you need
Using Tapatalk

User avatar
plumber_bob
KAC Member
KAC Member
Posts: 6774
Joined: Sun Feb 02, 2014 2:25 pm
Location: L.J. Ky
Has liked: 174 times
Been liked: 80 times

Re: Electrical light post question

Post by plumber_bob » Mon Nov 02, 2020 4:06 pm

iron369 wrote:
Mon Nov 02, 2020 3:56 pm
Toecutter1978 wrote:
Rem700 wrote:
Toecutter1978 wrote:
Mon Nov 02, 2020 9:24 am
Those gfci breakers are way larger than the standard breakers, I wonder if it will even fit in my panel.


Sent from my iPhone using Tapatalk
They make some GFCI breakers that fit in a single pole breaker location.... or at least they did.
Oh ok. Maybe the video I watched on how to replace one had to do with it being that it was one of those arc disruption breakers too.

That breaker was twice the size and from looking at my panel I do not know if it would fit behind it or not. I could see it not knowing my luck. I had to buy those slimmer gfci plugs that cost more because the plug boxes in the house are not the regular size or something.

Whom ever wired this place must have been I don’t know. Not an electrician.


Sent from my iPhone using Tapatalk
If you have a picture of your panel or some information about it, I may be able to direct you to the breaker you need